西门子MASTERDRIVE主控板CUVC及T400更换步骤

[复制链接]
wise_luo 发表于 2016-6-10 14:40:55 | 显示全部楼层 |阅读模式

CUVCT400更换步骤
1.      additionalinformations for changing of CUVC (over network/ Drive ES):
CUVC更换的附加信息(通过网络 / Drive ES

  • setting back to factory settings is not necessary if CUVC is     new
         如果CUVC是新的就没有必要设置回工厂设置
         
         
  • switch off the electronics power
断开电子模板的电源

  • disconnect Profibus
         断开Profibus的连接
         
         
  • replace CUVC
         更换CUVC
         
         
  • switch on electronics power supply (no Profibus connected)
         
    接通电子模板的电源(Profibus不要连接)
         
         

  • set P060 = 4, P918 = Profibus     address, P060 = 7
         
    设置P060     = 4,  P918 = Profibus 的地址,  P060 = 7
         
         

  • connect Profibus (all indicators are blinking of communication     is ok)
         
    连接Profibus(通讯正常的所有指示都在闪烁)
         
         

  • check model number:
检查模板的序列号
- if only CUVC is new, set P060 = 8, P070 = old inverter model number, P060= 7
如果CUVC板是新的,设置P060 = 8, P070 = 旧的逆变器序列号, P060 = 7
- if the complete inverter is new, this number isalready inside
  如果完整的逆变器是新的,这个序列号已经存在装置内


  • check electronics software version P069.1 = 3.x, should be 3.4,     otherwise upgrade the software / firmware version
         检查电子模板的软件版本P069.1 = 3.x,使其成为3.4, 否则,更新软件 / 固件版本
         
         
  • download the parameters
         
    下装参数
         
         

  • switch on the remaining fuses
接通其余的开关



2.     additional information for changingthe T400 technology board:

更换T400工艺板的附加信息



  • switch off the electronics power
         断开电子模板的电源



  • remove the T400 / exchange to new one; put the dongle /     software protection PAL into the new board
         
    拔出T400     将该T400板上的看门狗(dongle)或着叫软件保护器PAL取出,安装到新的T400板上(没有安装该保护模块的T400板可以被下装程序,但运行中会出现报错)。



  • switch on the electronics power
         接通电子模块的电源



  • open Simatic Manager
         打开Simatic Manager



  • change PG/PC setting in the Simatic Manager to DUST1 (COM1)     connection
         
    Simatic Manager中更改PG/PC设置为DUST1     (COM1)连接方式



  • compile hardware

编译(compile硬件组态



  • compile software (if problem     with Library, open project with Library and change the     CFC/Options/Customize/Compile options to “use Libraries from project”)

编译(compile软件(如果有Library问题,打开有Library的项目,然后改变CFC/Options/Customize/Compileoptions touse Libraries from project



  • download software, ignore error message, next window choose     “RESTART”
         
    下装软件,忽略错误消息,在下面出现的对话窗口中选择RESTART
         
         

  • open DriveMonitor, make new setting with T400 parameters     “SHEAR_LINES”

打开DriveMonitor,生成一个有T400参数的设置SHEAR_LINES


-> if “SHEAR_LINES” not exist, use “File/Learn Database” or go online andpress “Generate Database” to make new database

如果SHEAR_LINES不存在,使用File/Learn Database或者在线,然后按击Generate Database生成新的数据库



  • restart  power

重新启动电源(即将电子模板的电源关断后重新接通)



  • go online on CUVC

CUVC在线,其目的是要看T400的参数(即U 参数/H参数/C参数/L参数)




  • download T400 parameters      

下装T400参数



  • make Power On Reset
         
    在参数表的任务栏中选择“Power On     Reset



  • completed     结束



ATTENTION:

注意以下故障处理

·        the shear is not synchronized anymore

飞剪还不能同步


-> check parameter c704 if shear is in home position (1=yes, 0=no); if not,move to home position with jogging

首先检查参数表中的参数c704,如果此时飞剪不在起始位(1=起始位,0=非起始位)如果不在起始位,那么使用点动操作将飞剪调到起始位。


-> set parameter L728 to “1” and then to “0”again

随后将参数L728先置为“1”,再置回到“0”


-> shear is synchronized

此时飞剪达到同步





·        after compiling, you can not goonline any more

在程序被编译之后,不能在线看程序


way1 for going online use backup project without compiling

方法1:用没有编译的备份项目在线


way2after download and restart, online is ok

方法2:在下装和重启之后,在线功能正常