The Catapult DNP3 driver supports DNP 3.0 master communications for up to 1,000 DNP 3.0 slave devices, across 200 serial and/or IP channels. The driver operates as an OPC server for any control system that supports OPC.
In addition to being an OPC server, the driver is also a native GE Digital iFIX or CIMPLICITY driver, using a native interface to iFIX or CIMPLICITY systems.
General
Supports DNP 3.0 to Level 3 for both Requests and Responses
Sequence of Events (DNP Level 3 only)
Report by exception (DNP Level 3 only)
Slave supported DNP levels 1, 2, 3
Internet Protocol - both UDP and TCP
Serial (300-57600 baud)
Radio support includes Flow control; Push To Talk control; Pre & Post-transmission delay setting; configurable retries and timeouts
DCOM is not currently supported, the driver must run on the SCADA server
DNP3.0 for iFIX
Database addressing supports both IFIX (NIO) and OPC interfaces
The Driver can be started as a standard iFIX driver through the SCU, or configured to run as a windows background service.
DNP3.0 for CIMPLICITY
Database addressing supports both CIMPLICITY and OPC interfaces
The Driver can be started as a standard CIMPLICITY driver.
Devices & Channels
Separate configuration of devices and channels
Each device can be connected to one or more channels
Each channel can be connected to one or more devices
Prioritization and automatic fail over when multiple channels are available
The maximum number of channels and devices is limited by system resources. The driver has been tested up to 1,000 devices and 200 channels.
Sequence of Events (SOE)
SOE Level 3 time mode, supporting Local and UTC time
Each and every SOE detected and written to the SOE log file, time stamped to 1msec using time captured by the I/O device
Includes time synchronization
Full support for SOE event display in iPower SCADA
Momentary Change Detect
Momentary changes (e.g. closed>open>closed) can be captured and passed on to the SCADA system, regardless of master polling cycle speed.
Each momentary change is time stamped as it was captured by the I/O device, providing an accurate record of the change.
Configuration
”On the fly” configuration without requiring system restart
Logging
Communications monitoring in configuration window and to file Logging of raw binary data (data link) and decrypted data (application layer)
Comprehensive statistics for both devices and channels
Separate SOE log file
All statistics are available to SCADA
This electronic help provides descriptive material and specific operating procedures for performing all common tasks.
【必读】版权免责声明
1、本主题所有言论和内容纯属会员个人意见,与本论坛立场无关。2、本站对所发内容真实性、客观性、可用性不做任何保证也不负任何责任,网友之间仅出于学习目的进行交流。3、对提供的数字内容不拥有任何权利,其版权归原著者拥有。请勿将该数字内容进行商业交易、转载等行为,该内容只为学习所提供,使用后发生的一切问题与本站无关。 4、本网站不保证本站提供的下载资源的准确性、安全性和完整性;同时本网站也不承担用户因使用这些下载资源对自己和他人造成任何形式的损失或伤害。 5、本网站所有软件和资料均为网友推荐收集整理而来,仅供学习用途使用,请务必下载后两小时内删除,禁止商用。6、如有侵犯你版权的,请及时联系我们(电子邮箱1370723259@qq.com)指出,本站将立即改正。
|